Hot Water Circulation and Additional Flow
| 论文类型 | 技术与工程 | 发表日期 | 2005-10-01 |
| 作者 | Sheng,Guorong | ||
| 关键词 | circulating flow additional flow circulating-pump flow circulating-pump head | ||
| 摘要 | By analyzing the process of hot water circulating and the implication of additional flow,the weakness,lying in the definition of additional flow and in the calculation formula of circulating-pump head and circulationg-pump flow in current code,is pointed | ||
          Sheng Guorong
          ChongQing Architectural Design Instiute
          Add:No.31 Renhe Street, Yuzhong District, Chongqing Zip Code:400015
          Tel:023-63621179 Fax:023-63856935
ABSTRACT By analyzing the process           of hot water circulating and the implication of additional flow,the           weakness,lying in the definition of additional flow and in the calculation           formula of circulating-pump head and circulationg-pump flow in current           code,is pointed out. The implication of additional flow is also discussed.A           new opinion about calculationg the pump head and the pump flow is brought           brought forward.
           KEYWORDS circulating flow, additional flow, circulating-pump           flow,circulating-pump head
          1 Requirements of the code
          In curent Code for Design of Building Water Supply and Drainage(GBJ15-88),there           are mainly two stipulations to the circulating-pump in a central heating           flow,the circulating-pump head should as 15% of the maximum hourly hot-water           consumption;Secondly,the circulating-pump head should be counted as           Hb=(1+qf/qx)2.hp+hx[formula?],in which Hb is the circulationg-pump head           is the circulation flow;qf is the additional flow,hp and hx are the           head loss in distributing pipes and in is the circulationg flow;qf is           the additional flow,hp and hx are the head loss in distributing pipes           and in returning pipes respectively. In the code,the additional flow           is definged as follows: In a mechanical circulating hot-water flow should           be considered when calculating the head loss in the distributing pipes,           so as to prevent the circulation from being destroyed by the partial           water consumption. This water flow is called as an additional flow.
          In recent years, many queries focusing on the implication and calculation           the additional flow are put forward,but this seemed to have taken no           effect on the code. In this paper, these queries are to be discussed.
          According to the code, the formula for calculating the circulating flow           is :qx=(3600Qs)/(C.?t),where Qs is the heat loss,which can be counted           as 5%to 10%of the hourly heat consumption;C is the specific heat of           water;?t is the temperature difference. It‘s obvious that the circulating           flow is figured out on the assumption that there is no consumption occurring           in the hot water system, the purpose of circulating is to maintain the           temperature of the system.
           2. One opinion about the implication of additional flow
          According to formula?, when we calculate the circulating-pump head,           the head loss in distributiong pipes should be counted as (1+qf/qx)2.hp,this           indicates that not only the circulating flows, but also the additional           flow passes through the distributing pipes;while, the head loss in returning           pipes is still hx, this shows that the additional flow doesn‘t pass           through the returning pipes. Inthe definition, it‘s said that the additional           flow should be considered "when calculating the head loss in the           distributing pipes".Where the distributing pipes are mentined but           not are the returning pipes,this also indicates that the additional           flow passes through only the distributing pipes but not the returning           pipes.So it seems reasonable to think in this way: the additional flow           arises from the partial water consumption, and it approximately reflects           the small quantity of consumption. As shown in figure1, the flow is           replenished by cold water pipe. Since it is an approximate reflection           of partial water consumption, certainly it passes(or partially)through           the distributing pipes. It‘s also clear that it doesn‘t pass through           the returning pipes, because it‘s consumed, it doesn‘t take part in           the circulation really, it can‘t be called as an additional circulating           flow. From figure 1, it also can be found that the additional flow is           supplied from behind the circulating pump but not from before the pump,           it doesn‘t pass through the pump. The core of this opinion is that the           additional flow passes through only the distributing pipes but neither           the returning pipes nor the punmp,which is deduced from the code. But           this doesn‘t agree with another part of the code, which requires the           pump flow to be the summation of circulating flow and additional flow.           Since the additional flow doesn‘t pass through the pump,why must the           outflow of the pump be the summation of the circulating flow and the           additional flow as described in the code? A contradiction appears.
          Somebody says figure 2 can work, because the additional flow passes           through both the pump and the distributing pipes but not the retuming           pipes, which is in accordance with the code. But that manner is not           always feasible in most cases. In that manner, because the pump has           to be running all the time and the outflow might range between one-tap-flow           and a design flow, it‘s difficult to choose a centrifugal pump to meet           the request.
          3. Another opinion about the implication of additional flow
          According to the code, the additional flow is utilized to prevent the           circulation from being destroyed. So it appears logical to think in           this way:Because the circulating flow is figured out on the assumption           that there is no consumption in the hot water system, it can be called           as a "theoretical circulating flow"to which is resorted to           make up for the heat loss.When it‘s averaged to several vertical pipes           ,the circulating flow in each pipe may be very little. In order to keep           the circulation from being destroyd by partial consumption ,an extra           flow should be added to the theoretical circulating flow ,thus a "factual           circulating flow‘is gained. Because the flow in each pipe is enlarged,           the influence of the partial consumption is remarkably reduced. Consequently,           the circulation effect is ensured. This extra flow is just the "additional           circulating flow".Being understood in this way, the additional           flow is not an approximation of the partial consumption but an extra           flow added to the theoretical circulating flow.It passes through the           pump, the heat exchanger, the distributing pipes and the returning pipes,           therefor it takes part in the circulation really and can be called as           an additional circulating flow. Since it passes through the returning           pipes, certainly the head loss in returning pipes ought to be counted           as (1+qf/qx)2.hx but not hx yet.Thecore of this opinion is that the           additional flow passes through the entire pipe-loop of the pump should           be summation of the circulating flow and the additional flow",but           it conflicts with formula(1) in calculating the head loss in returning           pipes. This opinion can‘t make the code justify itself none the less.
           4 Comparison of the two opinions
          The implications of "additional flow"are quite different in           above two opinions. According to the former one ,the cold water pipe           replenishes the additional flow, and this flow is consumed in the distributing           pipes, so it seems more exact to call the flow an "additional distributing           flow"(qpf)than to call it an "additional circulating flow".To           the latter opinion ,the additional flow does take part in the circulation,           it can be called as an " aadditional circulating flow"(qxf).The           two different implications are both referred to in the code, but they           are not told from each other. If it‘s necessary to keep the circulation           from being destroyed and properly figure out the head loss in the pipe-loops,both           the two kinds of additional flows ought to be taken into account, namely           Hb=[1+(qpf+qxf)/qx]2.hp+(1+qxf/qx)2.hx[formula?].If the factual circulating           flow is shown as qsx(namely qsx=qpf+qxf),the head loss in distributing           pipes and returning pipes are shown as hsp and hsx respectively, from           formula? the following formula is derived; Hb=(1+qpf/qsx)2.hsp+hsx[formula           ?].formula?resembles formula ? formally.
          5 Examples
          In a section of a hotel, the parameters are as follows:n=280beds, q=200l/bed.d,           Tr=60?,T1=7?,?t=10? and Kh=5.73, thus Qh=13.4m3/h;If Qs is estimated           as 7% of the maximum hourly heat consumption, then qx=5.0m3/h. When           qx is averaged to the 10 vertical pipes, the circulating flow in each           pipe is 0.5m3/h. As the diameter of inlet and outlet are DN50 and DN25           respectively, the velocities of inlet and outlet are Vi=0.07m/s and           Vo=0.28m/s respectively. Considering the qf which is counted as 15%           of the Qh according to the code,the total factual circulating flow is           enlarged to be 0.7m3/h?then the velocities are Vi=0.10m/s and Vo=0.40m/s.
          In a section of a hospital, each original parameter is the same as above           except Kh=2.66. Then the results are Qh=6.2m3/h and qx=2.3m3/h, accordingly           Vi=0.03m/s and Vo=0.13m/s. Appended with the qf, the velocities are           Vi=0.05m/s and Vo=0.18m/s.
          From above, it‘s easy to find that in a hotel, no matter the additional           flow is considerd or not ,the velocity in each vertical pipe changes           little; with the same Qh, the more are the vertical pipes, the more           will the velocity decrease. Ina hospital, as the Kh is much smaller           than in a hotel, the velocities are much lower even if the additional           flow is considered.
           6. Factors influencing the effect of circulation
          What on earth is the disadvantage of a too low velocity? As we know,           although each pipe-loop is designed to be nearly alike, the circulating           velocities may be very different ,we have to make them nearly identical           by the conditioning of the valves. If the velocities are too low,it           will be very difficulty to ensure a certain quantity of flow passing           through the pipes and avoid any short-circuiting. Unfortunately, from           above example of a hospital, we can see that even if the additional           flow is considered according to the code,the disadvantage is not avoided.           That means the destruction of circulation can‘t avoided.
          If the circulating velocity is not very low, will the partial water           consumption destroy the circulation ? Let‘s analyze it referring to           figure 1. If there‘s a consumption near the inlet of a vertical pipe(as           at point A),because the pipe diameter is relatively big enough ,the           circulating flow in this pipe won‘t be influenced remarkable, the circulation           of the whole pipes is not destroyed .If the consumption is near the           outlet of the pipe(as at point B), because the pipe diameter is relatively           small,the circulating flow in this pipe will must decrease and the circulation           of the pipe seems destroyed. But the total flow of the pipe increases,the           heat loss is compensated for, the "destruction"doesn‘t matter;           and the circulating flows in other pipes increase a little. In the same           way ,if the consumption is at the middle of the pipe(as at point C),the           total flow during point A and point C increases, and the total flow           (circulating flow )during point C and point B decreases a little. It           is clear that the nearer is the consumption point to the inlet ,the           less is the influence to the circulation; the nearer is it to the outlet,           the shorter is the influenced pipe.
          Above analysis shows: although the partial consumption may reduce the           circulating flow in a vertical pipe, the total flow of the pipe won‘t           decrease. So the heat loss can be compensated for, the destruction doesn‘t           harm the purpose of circulation. The more is the consumption, the better           is the circulation effect. So long as the circulation can be ensured           with no partial consumption, even if the partial consumption occurs,           the effect of circulation can be ensured all the same. What really matters           is how to ensure the circulation with no consideration of the partial           consumption.
          7 Conclusions
          The additional flow is just adopted to ensure an appropriate factual           circulating flow so that the circulation can be ensured; therefor the           determination of an additional flow is of significant sense.From my           point of view, when we determine the outflow of a circulating pump,the           theoretical circulating flow should be figured out first according to           the code,then the circulating velocity of each pipe must be verified.           If it‘s not very low, the additional flow needn‘t be considered. Otherwise,           if it‘s too low, the additional flow should be added to the circulating           flow, thus we can get a factual circulating flow that can be the outflow           of the pump. the pump head needn‘t be counted as formula?. So an appropriate           circulating velocity determines the additional flow. What velocity can           be regarded as an appropriate one? This depends. As in above example           of a hotel, the outlet velocity of 0.3m/s or so (counted according to           the code)is acceptable; it‘s also proved feasible by many other practical           projects. But it‘s not the case in a hospital, the additional flow should           be determined according to an appropriate velocity(for instance, 0.3m/s)           but not to the code.
          All in a word, the circulating velocity determines if an additional           flow should be taken into account; and the quantity of the additional           flow should also be determined by nthe verification of the velocity           so as to get an appropriate factual circulating flow. Only in this way           can the effect of circulation be ensured.
相关推荐
- MAXFLOW叶轮在高密度沉淀池工艺上的应用
- Performance of simultaneous nitrification and denitrification in lateral flow biological aerated filter
- Visual MODFLOW在平原型水库水环境数值模拟中的应用
- Hunters Probability Method Applied to Determine Water Supply
- Thinking about Putting up Reservoir in High Rise Building
- The Consideration on Revision of "Code for Design of Buildin